Humidity value/sensor

systematsystemat
edited September 2008 in InfraSensing Sensors
Serverscheck version 7.12.0, environmental sensors only.

Used : T°&Humidity sensor

The humidity warning value is on : less than 10rH or greater than 75rH.

The DOWN values are on : less than 75rH or greater than 80rH.

Warning setup is : "only when warning with a returned value".

PROBLEM : We get always warnings with a returned value as 54,5rH.

But the rH is not less than 10rH and not greater than 75rH.

QUESTION : Why this warning appears always?

Thank you for your answer

Comments

  • AdministratorAdministrator
    Allow me first to point out that the tresholds are very low and very high. Best practice is to have humidity between 45% rH and 65 %rH Below 45% rH may result in ESD and above 65% rH you risk corrosion.



    Your down values are incorrect. The lower limit has to be lower compared to the lower warning limit. 54.5 is always less than 75%rH (lower limit DOWN)



    Run the s-server.exe in debug mode and click on test settings. Reply with the output sent.
  • systematsystemat
    Hi,



    There is an error in my last post:

    The DOWN values are on: less than 10rH or greater than 85rH



    How to run s-server.exe in debug mode?



    Sincerly,
  • systematsystemat
    Hi,



    Here is the result of debug:

    # Running in test mode

    # test Fri Oct 3 07:41:29 2008 TEST - Starting check

    # test Fri Oct 3 07:41:29 2008 C10.1.0.21.log removed (A)

    # test Fri Oct 3 07:41:29 2008 COM10.1.0.21 free - starting reading

    # Fri Oct 3 07:41:33 2008 Serving Wizard 4_1

    # test Fri Oct 3 07:41:35 2008 reading log

    # test Fri Oct 3 07:41:36 2008 0 Device Model = Temperature/Humidity Sensor

    # test Fri Oct 3 07:41:36 2008 1 Device Status = Normal

    # test Fri Oct 3 07:41:36 2008 2 Firmware Version = 5.00

    # test Fri Oct 3 07:41:36 2008 3 Number of variables = 5

    # test Fri Oct 3 07:41:36 2008 4 Variable 1: HUMIDITY (1 % RESOLUTION) 54 % RH

    # test Fri Oct 3 07:41:36 2008 5 Variable 2: HUMIDITY (0.1 % RESOLUTION) 53,9 % RH

    # test Fri Oct 3 07:41:36 2008 6 Variable 3: TEMPERATURE (0.5 C RESOLUTION) 22 C

    # test Fri Oct 3 07:41:36 2008 7 Variable 4: TEMPERATURE (0.1 C RESOLUTION) 22,1 C

    # test Fri Oct 3 07:41:36 2008 8 Variable 5: HASH ID 38031

    eq true and 0>=300

    # test Fri Oct 3 07:41:36 2008 TEST - OK - - 53.9

    # Fri Oct 3 07:41:38 2008 Serving Wizard 4_1



    Here is the alert message that I receives:

    Thu Oct 2 20:30:48 2008. Motif: Error: Warning level: 53.6 (returned value) greater than 10|75 .



    Sincerly,
  • AdministratorAdministrator
    The test shows it runs fine so the issue must be in a different component.



    Please run the sensor against the trial version of latest release of the software (7.14) and report back