I am using a sensor gateway and the value for my flood is showing as the temperature. I have updated to monitoring software to 9.0.6.
Thanks,
Jenna
Comments
Administrator
A fix is coming in the future for the freeware version
Currently you have to either create a SNMP check or SNMPSTRING check and use the correct OID. For Flood this would be a SNMPSTRING check
If you don't know the OID then add the SensorGateway as a new device. Once created, click on SNMP WALK button in the device details page and select the correct OID.
Jenna
Is there an estimated time on when there will be a fix?
Comments
Currently you have to either create a SNMP check or SNMPSTRING check and use the correct OID. For Flood this would be a SNMPSTRING check
If you don't know the OID then add the SensorGateway as a new device. Once created, click on SNMP WALK button in the device details page and select the correct OID.
THANKS!